OMETH Driver with CP1L Ethernet Communication
Last Post 17 Sep 2019 11:02 AM by Norman E. 9 Replies.
Printer Friendly
  •  
  •  
  •  
  •  
  •  
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Author Messages
EkoriantoUser is Offline
Basic Member
Basic Member
Posts:10


--
04 Sep 2019 01:11 AM
    Hi All,

    I need help in communication between Omron PLC CP1L series by Ethernet Connection.
    My CP1L IP Address is 172.17.33.44 with Network 1 & Node 4.
    My Computer IP is 172.17.33.1.
    Hereby i attached the configuration I've made on the Cx-Programmer and Indusoft.
    Really thx for your big help.
    Thx.

    Best Regards,

    Ekorianto:):)

    CP1La.pngCP1L.PNGOMETH.PNG
    ElectrocontrolUser is Offline
    Basic Member
    Basic Member
    Posts:19


    --
    04 Sep 2019 10:56 AM
    Try 172.17.33.44:9600:0:0. It works for me.


    EkoriantoUser is Offline
    Basic Member
    Basic Member
    Posts:10


    --
    04 Sep 2019 08:44 PM
    Hi,

    Thx for the reply.
    I have try 172.17.33.44 and still no result.
    Read Status error is -15.
    (File attached below)

    Just info, i have tried read and write from Indusoft by using OMRON driver, but i want to change by using OMETH driver, but its failed.
    Really need help for this one.
    Thx.

    OMETH1.PNGResult.PNG
    EkoriantoUser is Offline
    Basic Member
    Basic Member
    Posts:10


    --
    10 Sep 2019 08:57 PM
    Hi,

    Still need some help regarding this issue.
    Thx.


    ElectrocontrolUser is Offline
    Basic Member
    Basic Member
    Posts:19


    --
    11 Sep 2019 04:39 AM
    Can you do a ping from the PC to the PLC?


    Norman EUser is Offline
    Advanced Member
    Advanced Member
    Posts:37


    --
    12 Sep 2019 02:01 PM
    I do not use Omron but, according to the driver manual, since you are using network 1 then you need to set the Station to 1 on the Advanced settings of the OMETH driver.


    EkoriantoUser is Offline
    Basic Member
    Basic Member
    Posts:10


    --
    15 Sep 2019 09:40 PM
    Yes, i can ping the PLC from my PC for sure.

    You mean the station should be set to 1:1 or 1, i have do that both and still cannot communicate.


    Norman EUser is Offline
    Advanced Member
    Advanced Member
    Posts:37


    --
    16 Sep 2019 02:08 PM
    Are you trying to use the OMRON and OMETH drivers on the same machine at the same time? It is possible that all of the OMETH traffic is being intercepted by the OMRON (Sysmac/FINS gateway) driver, especially if they are using the same port/network/node settings. If you are, try changing the port number and node for the OMETH driver.

    You can also try to increase the start message timeout setting.


    EkoriantoUser is Offline
    Basic Member
    Basic Member
    Posts:10


    --
    16 Sep 2019 08:31 PM
    Hi Norman,

    Thx for the reply.
    I'm only use OMETH driver without any Omron Drivers in a PC.

    I have tried increase the start message timeout setting and still failed to communicate.
    Really need some help.
    Maybe i miss something that i didnt know, i can do some screenshot if needed.
    Thx.


    Norman EUser is Offline
    Advanced Member
    Advanced Member
    Posts:37


    --
    17 Sep 2019 11:02 AM
    I guess what I was asking is if Sysmac gateway or fins gateway was installed on the Indusoft PC? (you do not need them for OMETH)
    You can still try changing the port number and/or node number to see if it helps.
    What OS are you using?
    Is the firewall disabled? (you may need to allow port 9600)
    Is the 'Driver Runtime' task set to automatic?
    What do you see in the output window if you enable 'Field Read Commands' on the output window settings?